Jimmy,
A suction pressure of 30psi when the compressor is engaged indicates an evaporator temperature of 35 deg, a little too low. Either the system is low on charge, or like Lee says you have no airflow across the evaporator coil, or the orifice tube is plugged. If the fan is blowing air out the registers, you need to check the air doors to be sure they are directing air across the evaporator coil and not the heater core (or if the heater has a vacuum water valve, that the valve is closed).
Without a high side pressure reading, hard to tell if you have a plugged orifice tube or not. A plugged tube will cause a very high discharge reading, and could be causing the compressor to cycle, if the system has a high pressure cutout switch (some do not, they just have a burst disk that pops).
Recommend you do NOT try adding any more refrigerant until you get a high-side reading.