captaincarpet
Member
If you plan on using the air movers for flood work, The first thing to look at is the amperage draw the fan has. Most 3,000-3500 cfm airmovers draw 10-12 amps EACH, so in order to place 4 in a room you will need a 50 amp circuit at least! ( don't forget 80% rule). That is just for 1 room, 3 or 4 room floods would require hooking directly into the houses main breaker box (and an electrician to do this) or bringing a generator on site at a great additional cost per day that no one will want to pay for.
Jon Don sells their 4.8 amp draw temptest air movers for 149.99
buy 30 only 145.94 each or buy 100 + for 139.94 each.
However even with these 4.8 amp draw airmovers you need a 25 amp circuit to run just 4 using the 80% rule to avoid burning down any homes.
We find that using a combination of both the typical centrifugal airmovers and the newer style Axial fans which draw 2-2.5 amps each allows us to dry without any risks (staying within the 80%) and for the most part without any auxiliary power source.
When you do the math for the airmovers... don't forget to factor in the dehumidifier power consumption as well.
Jon Don sells their 4.8 amp draw temptest air movers for 149.99
buy 30 only 145.94 each or buy 100 + for 139.94 each.
However even with these 4.8 amp draw airmovers you need a 25 amp circuit to run just 4 using the 80% rule to avoid burning down any homes.
We find that using a combination of both the typical centrifugal airmovers and the newer style Axial fans which draw 2-2.5 amps each allows us to dry without any risks (staying within the 80%) and for the most part without any auxiliary power source.
When you do the math for the airmovers... don't forget to factor in the dehumidifier power consumption as well.