The difference between a 90° mitered ell and a smooth sweep is well-documented in the air duct world. They figure losses as
equivalent length (EL) - in other words if a fitting has an EL of 50 it means the fitting causes as much loss as adding 50 feet of straight duct.
Although round air ducts are not usually smaller than 4" the results would be very similar for any round hose/fitting.
A smooth 90° swept ell with a radius at least 1.5 times the diameter has an approximate
EL of 10 (for a 2.5" ell this would be a bend radius of around 4").
A 90° mitered fitting made by cutting straight pipe at a 45 and joining them together has an approximate
EL of 75. It's like adding 75 feet of hose to your existing hose run.
In other words, switching from a mitered elbow to a smooth elbow would give you the same performance gain as chopping 65 feet off your hose run (!). Not earth shattering, but not trivial either.