The Limit?

Willy P

Member
Joined
Oct 2, 2007
Messages
10,745
Location
Vancouver
Name
Willy P
I replaced the limit switches or thermostats on my 2 cord electric heater. 2 of them are 230 2 are 190. Would it blow up if I stuck in 4 230 switches? Shut off is supposed to be 200.
 

Jim Martin

Supportive Member
Joined
Oct 7, 2006
Messages
10,878
Location
Arizona
Name
Jim Martin
yes..........

190 is the low limit.....meaning that once the heater cuts off the fan needs to cool the coils down to 190 before the limit switch trips out the fan

230 is your high limit...meaning that the coils can get no hotter then 230 before the fan kicks on..this allows you to get as much heat from the unit with out blowing a bunch of cold air while it is trying to heat up...

if you were to switch the 190 to 230 then the fan would not cool the electric coils and they would burn in half...the coils are at there hottest point when they shut off..this is one reason why it is important to cool them down.........
 