Freezing Regulators - Frost on LP Gas Regulator
During normal operation propane regulators can become covered in frost, which may alarm some users. While this "freezing" of the regulator may be a symptom of an actual problem, it usually is a sign that outside humidity is at a level capable of producing condensation. The only difference is, the condensation forming on a regulator is frozen. As described, propane regulators act as a barrier between high tank pressures and delivery pressure as required by downstream appliances and/or equipment.
Once a propane appliance is actively in use, the liquid propane in a tank or cylinder begins to boil. The propane vapor, as boiled off the top of the liquid begins its journey downstream to the point at which it is used. Before making its way to the LP Gas system piping, it passes through the regulator where its pressure is reduced to a usable level. Keep in mind that the regulator will only deliver a constant pressure on the outlet side while inlet pressures can significantly vary. As the propane passes through the regulator, it expands (resulting in sub zero temperatures) and causes the regulator to gradually reach the extremely cold temperature of the propane vapor passing through it. Depending on the temperature and humidity of the surrounding air, the regulator will produce condensation, much like that of a frozen mug or glass taken out of a freezer.
This is why, under normal operation in hot and humid climates, the external surface of a regulator will freeze and appear to be frozen or frosted. The rate at which propane is being withdrawn from the tank or cylinder will also cause the container to display a visible frost line, which indicates the liquid level of the propane within the tank.
Maybe I should of googled first.
Can the brass crack and cause a leak?
Thanks